    More Energy Efficient Shop Lighting

    I currently have 51 T12 48" 2 lamp shop lights in my shop.
    I am looking into changing to some more energy efficient lighting.
    I read that T8 & T5 lights are more energy efficient than the T12s. I am confused on how they are more energy efficient when they use the same wattage bulbs.
    I was taught that wattage is energy used, so how does the same wattage use less energy?

    The current shop lights are plugged into outlets in the ceiling. I am also toying with the idea of getting plug in light socket adapters & LED flood light bulbs to plug into the outlets to see how they would light the shop. What I like about this idea is that it would cost less for the conversion & some of the LED bulbs have the color of incandescent bulbs.

    The ceiling in most of the shop is 9' 6". another part has a cathedral ceiling that starts at 9' 6" & goes up to 12'.

    I did a calculation of energy use if I was to go with all LED bulbs. That would cut my electric bill by about $87 a month.

    I have no idea how to figure what the energy cost difference would be to convert to T8 or T5 lights.
    Kioti CK3510SE HST, Kioti KL4030 Loader, John Deere 655 Tiller, Frontier LR2072 Landscape Rake, Virnig V50 Pallet Forks, Woods GB60 Box Blade
    John Deere X739 AWS 4X4, 60HC Auto Connect Deck, Front grader blade.
    John Deere 825i Gator

    John Deere Tractors I have owned in the past.
    425 AWS, 455, 4400, 2210, 4710, 2320, 2720, X475, 1026R, 4120, 2025R

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2
    rgd
    rgd is offline
    rgd's Avatar
    Join Date
    Mar 2011
    Last Online
    02-18-2019 @ 10:52 AM
    Location
    Flint, Texas
    Posts
    2,160
    Thanks
    317
    Thanked 227 Times in 182 Posts
    Quote Originally Posted by ChrisR View Post
    I currently have 51 T12 48" 2 lamp shop lights in my shop.
    I am looking into changing to some more energy efficient lighting.
    I read that T8 & T5 lights are more energy efficient than the T12s. I am confused on how they are more energy efficient when they use the same wattage bulbs.
    I was taught that wattage is energy used, so how does the same wattage use less energy?

    The current shop lights are plugged into outlets in the ceiling. I am also toying with the idea of getting plug in light socket adapters & LED flood light bulbs to plug into the outlets to see how they would light the shop. What I like about this idea is that it would cost less for the conversion & some of the LED bulbs have the color of incandescent bulbs.

    The ceiling in most of the shop is 9' 6". another part has a cathedral ceiling that starts at 9' 6" & goes up to 12'.

    I did a calculation of energy use if I was to go with all LED bulbs. That would cut my electric bill by about $87 a month.

    I have no idea how to figure what the energy cost difference would be to convert to T8 or T5 lights.
    Sounds like you know how to figure cost but are missing a couple of figures. I believe you are missing the ballast factor /drain/wattage to fire off those 32 watt bulbs. If you can find that difference in power usage , you should be able to figure the rest. I'd do it but I am currently really sick and having a hard time concentrating..
    JD 2520 TLB
    JD gt 275

    Always remember that you're unique. Just like everyone else.

  4. Top | #3

    Join Date
    Jun 2014
    Last Online
    Today @ 08:44 AM
    Location
    Berlin, MA
    Posts
    4,604
    Thanks
    94
    Thanked 869 Times in 664 Posts
    Also missing here is the brightness factor. A 32-watt bulb is indeed a 32-watt bulb, but each puts out a different amount of light as measured in lumens. A bulb that puts out 1000 lumens at 32-watts is more efficient that a bulb that puts out 600 lumens at 32-watts.

    Light efficiency is measured as "Lumens per Watt" or "LPW"

    T12=78 LPW
    T8=90 LPW
    T5=99 LPW


    To put that is layman's terms - for the same 32-watts consumed, you get a lot more light out of a T8 or T5 bulb than you do from a T12. In theory, if the lighting with a 32-watt T12 is adequate, then you could drop down to a 26 or 28-watt T8 and get the same amount of light.
    arlen, rtgt, OxPath and 1 others like this.
    D160 Mower/Bagger.
    2014 2032R tractor/H130 FEL w/Bolt-On Hooks/54" Snow Plow/iMatch Quick-Hitch/County Line 5' Scraper blade/County Line Carry-All/Artillian 42" Forks & QH Adapter/JD Ballast Box/Frontier SB1164 3PH Blower/Leinbach PHD/Wallenstien BX42 Chipper

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    felixm22's Avatar
    Join Date
    May 2013
    Last Online
    07-21-2019 @ 01:57 PM
    Location
    Concord, NH
    Posts
    3,964
    Thanks
    320
    Thanked 453 Times in 340 Posts
    I agree with above. It is also fairly easy to switch from T12 to T8. All you need it to swap out the ballasts. I converted some old 4' 4 lamp fixtures that my old job was going to scrap.


    Sent from my iPhone using Tapatalk
    John Deere 318, 50in deck, 54in blade w/ power angle

    Looking for JD Parts check here on JD's official parts website.

    Have no idea where to start with JD Parts check here for a how to.

  7. Top | #5
    Tomfive's Avatar
    Join Date
    Dec 2011
    Last Online
    Today @ 07:26 AM
    Location
    Mid-Hudson Valley, NY
    Posts
    4,147
    Thanks
    97
    Thanked 606 Times in 471 Posts
    At work, we made a switch quite a few years back from T12's and mercury vapor to T5's. Now we're moving to LED lighting, they seem a little harsh at first, but the workers are getting used to them. I don't know the savings from each move, but the LED fixtures are pricey.

    We're moving to more and more LED lighting at home. For my garage, and basement, I started to move from T12's to T5's but it seems that The T5 bulbs were quite a bit more expensive that the T12's. And it seems that the T5's had a shorter life. May just be my imagination.

    I'm saving my pennies for LED lighting, it seems to be the wave of the future.

    Just my 2 cents.
    johnH123 likes this.
    Tom

    2011 1026R/R4's -- H120 FEL/49" -- 260 BH/12" -- Bro-Tek Ripper -- Artillian Forks/42" -- 244 lbs JD Rear Wheel Weights -- KBOH Hooks and Clevis' --
    Block heater -- 180* T-stat -- Evans HP Waterless Coolant

  8. Top | #6
    RandyM's Avatar
    Join Date
    Sep 2010
    Last Online
    03-14-2017 @ 10:30 AM
    Location
    Stoughton, Wisconsin
    Posts
    6,594
    Thanks
    1,047
    Thanked 1,061 Times in 672 Posts
    Quote Originally Posted by Tomfive View Post
    I'm saving my pennies for LED lighting, it seems to be the wave of the future.

    Just my 2 cents.
    I agree. LED, everything else is old inefficient technology. It is a bit pricey now, but that will change too.
    Randy __________________________________________________ ___ Be Safe!

    2009 - 2305 w/62 MMM **** 2008 - 2520 w/72 MMM **** 200CX w/49 bucket
    Weight Box w/extension ***** LandPride RTR 1558 Tiller ******* 54 Snow blower
    60 Gallon Demco Sprayer *** 60 Broom ** BB2060 Box Blade**SS2036B Spreader
    Everything Attachments ETA-PluggerV2-60 Aerator

    The more I learn, the less I know.

  9. Top | #7

    Join Date
    May 2013
    Last Online
    11-06-2017 @ 10:30 AM
    Location
    Linn, MO
    Posts
    139
    Thanks
    3
    Thanked 11 Times in 11 Posts
    LED is the way to go! Focus on lights that get used the most, and convert them to LED first. We just built a new home and put LED everywhere except closets and a couple spots that rarely get used. I can already see it paying dividends!
    JD 2720 nicely equipped with FEL, MMM, 4' Land Pride Rotary Cutter, 5' Land Pride Blade

  10. Top | #8
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 08:33 AM
    Location
    Westminster, MD
    Posts
    16,254
    Thanks
    4,995
    Thanked 4,035 Times in 2,514 Posts
    I didn't go for "energy efficient", I went for Lumen's. When I need to see, I don't care if its costing me a few more pennies and hour-I need to see!

    T5's in the basement workshop, and T5HO's in the garage and pole barn.
    dieselshadow and Bill Berger like this.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  11. Top | #9

    Join Date
    Jun 2014
    Last Online
    Today @ 08:44 AM
    Location
    Berlin, MA
    Posts
    4,604
    Thanks
    94
    Thanked 869 Times in 664 Posts
    I have T8's in my garage and I'm about to swap them out for LEDs. Not so much concerned with energy use but The T8s still take a few minutes to warm up in the unheated garage. It's just a little frustrating when I go out there for something fairly quick and have to wait for them to warm up to get full light output.
    D160 Mower/Bagger.
    2014 2032R tractor/H130 FEL w/Bolt-On Hooks/54" Snow Plow/iMatch Quick-Hitch/County Line 5' Scraper blade/County Line Carry-All/Artillian 42" Forks & QH Adapter/JD Ballast Box/Frontier SB1164 3PH Blower/Leinbach PHD/Wallenstien BX42 Chipper

  12. Top | #10

    Join Date
    Jan 2012
    Last Online
    Today @ 06:11 AM
    Location
    East Central Indiana
    Posts
    1,470
    Thanks
    93
    Thanked 240 Times in 172 Posts
    Thanks everyone. Great information.
    I will post some updates later.
    Kioti CK3510SE HST, Kioti KL4030 Loader, John Deere 655 Tiller, Frontier LR2072 Landscape Rake, Virnig V50 Pallet Forks, Woods GB60 Box Blade
    John Deere X739 AWS 4X4, 60HC Auto Connect Deck, Front grader blade.
    John Deere 825i Gator

    John Deere Tractors I have owned in the past.
    425 AWS, 455, 4400, 2210, 4710, 2320, 2720, X475, 1026R, 4120, 2025R