    Electricity to shop

    So we should be ready to get wired upon the shop/garage by the end of next week. The stub into the shop is about 15 ft from our breaker box for the house which has 8 open slots

    I'll consult with an electrician when I get someone out to look at it, but just wanting some opinions on options.

    Full disclosure, I know very little about anything electrical so some of what I suggest may not even be possible.

    I'm assuming we have two options...either add breakers to the house box and wire everything in from those, or come off the main at the house box and install a breaker box inside the shop and go from there. I'm trying to figure out if one has any advantage over the other, cost, ease, or some added convenience that I haven't thought of. Which route would y'all take? Thanks!

    Sent from my SM-G930V using Tapatalk
    2017 3038E; RC2048, 4' Box Blade, Forks, 5' Rear Blade, 2017 Z920M

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2

    Join Date
    Jan 2017
    Last Online
    Today @ 03:16 PM
    Location
    Warner Robins, Georgia
    Posts
    504
    Thanks
    9
    Thanked 41 Times in 37 Posts
    Quote Originally Posted by userjh160 View Post
    So we should be ready to get wired upon the shop/garage by the end of next week. The stub into the shop is about 15 ft from our breaker box for the house which has 8 open slots

    I'll consult with an electrician when I get someone out to look at it, but just wanting some opinions on options.

    Full disclosure, I know very little about anything electrical so some of what I suggest may not even be possible.

    I'm assuming we have two options...either add breakers to the house box and wire everything in from those, or come off the main at the house box and install a breaker box inside the shop and go from there. I'm trying to figure out if one has any advantage over the other, cost, ease, or some added convenience that I haven't thought of. Which route would y'all take? Thanks!

    Sent from my SM-G930V using Tapatalk
    If it was me, I would have a panel in the shop.
    Tomfive, keane, userjh160 and 1 others like this.
    2018 1025r. 260B backhoe, 120r loader, Titan 36" forks, Frontier RT1142 tiller
    1995 Lowes branded riding mower.

  4. Top | #3
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 03:09 PM
    Location
    Westminster, MD
    Posts
    16,258
    Thanks
    4,996
    Thanked 4,035 Times in 2,514 Posts
    Your option #2 is best, it's called a "subpanel" if you want to search some-lots of threads here and on the net about adding one.
    This is best in my opinion because it will leave you 6 open slots in the house panel, and the circuits for the shop will be in the shop. I'd suggest a 100 panel so you have room to expand.
    etcallhome, Tomfive, arlen and 2 others like this.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  5. The Following User Says Thank You to Kennyd For This Useful Post:

    userjh160 (07-06-2019)

  6. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  7. Top | #4

    Join Date
    Mar 2018
    Last Online
    Today @ 01:10 PM
    Location
    Ontario, Canada
    Posts
    313
    Thanks
    47
    Thanked 31 Times in 30 Posts
    I can only tell you how I did it here in Ontario. I only needed 20 amps at the garage so I put a double pole 20 amp breaker in the main panel and wired 3-wire #8 from there underground to the garage about 130 feet away. I used pvc conduit to go through the floor into the crawl space and under the foundation. It's then direct buried to the garage and through pvc under and through the garage floor to a 30amp disconnect with two 20 amp screw-in circuit breakers. I then ran #12 3 conductor the length of the garage, one hot leg for lights and the other for outlets. It was cheaper to use the double pole breaker at the main box, than put a pony panel there, and another in the garage. Good Luck. One thing, if you do it yourself, get it inspected. If you don't and there's an electrical fire, the insurance company may deny your claim.
    Last edited by NotYourGrandfathersDeere; 07-06-2019 at 10:04 AM.
    Toughsox likes this.

  8. The Following User Says Thank You to NotYourGrandfathersDeere For This Useful Post:

    userjh160 (07-06-2019)

  9. Top | #5

    Join Date
    Jun 2014
    Last Online
    Today @ 03:04 PM
    Location
    Berlin, MA
    Posts
    4,604
    Thanks
    94
    Thanked 869 Times in 664 Posts
    I believe the electrical code requires you have a panel in the garage if you plan on running more than 1 circuit.

    Not having a sub-panel is silly anyway, IMO. Do you want to run back into the house every time you trip a breaker? A sub-panel in the garage is usually cheaper in the long run and is always more convenient.
    Toughsox likes this.
    D160 Mower/Bagger.
    2014 2032R tractor/H130 FEL w/Bolt-On Hooks/54" Snow Plow/iMatch Quick-Hitch/County Line 5' Scraper blade/County Line Carry-All/Artillian 42" Forks & QH Adapter/JD Ballast Box/Frontier SB1164 3PH Blower/Leinbach PHD/Wallenstien BX42 Chipper

  10. The Following User Says Thank You to JimR For This Useful Post:

    userjh160 (07-06-2019)

  11. Top | #6
    iamrfixit's Avatar
    Join Date
    Apr 2019
    Last Online
    Today @ 01:55 PM
    Location
    Iowa
    Posts
    48
    Thanks
    3
    Thanked 21 Times in 14 Posts
    Quote Originally Posted by userjh160 View Post
    So we should be ready to get wired upon the shop/garage by the end of next week. The stub into the shop is about 15 ft from our breaker box for the house which has 8 open slots

    I'll consult with an electrician when I get someone out to look at it, but just wanting some opinions on options.

    Full disclosure, I know very little about anything electrical so some of what I suggest may not even be possible.

    I'm assuming we have two options...either add breakers to the house box and wire everything in from those, or come off the main at the house box and install a breaker box inside the shop and go from there. I'm trying to figure out if one has any advantage over the other, cost, ease, or some added convenience that I haven't thought of. Which route would y'all take? Thanks!

    Sent from my SM-G930V using Tapatalk

    You definitely want a sub panel in the new shop, it makes things much easier in the long run. My shop includes a two stage compressor and large mig welder as well as several woodworking machines, table saw, shaper, planer, drum sander and dust collector, all these are large 240v machines. Since I'm a one man shop, I almost never run more than two machines at a time so I get by just fine with a 60 amp service to my shop. On rare occasions my compressor might kick on while I'm using one of the machines and running the dust collection, so it's sized to handle that along with all the lights and plenty of room to run a couple fans and whatever else might be running.

    Very simple to do and most of the cost will offset when compared to the labor and material to run numerous circuits the extra distance into the house. This way you have a nice starting point for your wiring in the shop and you won't fill up all the available slots in the main panel. You install the appropriate sized breaker in the house and size the wire according to that breaker and the distance to your shop. I have a 60 amp breaker and four #6 copper THHN, running through conduit about 50 wire feet to my shop. Two of the wires are hot, one is neutral and one is a ground that will bond the panels. The neutral and ground bus are separated at the sub panel and the neutral bonding screw should be installed at the main panel but removed from the sub panel. All of your receptacles and lights must have the neutral wires connected to the neutral bus bar, and the ground wires connected to the separate ground bar.
    Tomfive and Toughsox like this.
    2008 John Deere 2305, 200CX loader, 62C mower deck, imatch, 647 Tiller
    2005 John Deere X495, 62C mower deck and 54" snow blade
    1977 John Deere 300 garden tractor with 48" deck, 33 tiller and home built hydraulic blade

  12. The Following User Says Thank You to iamrfixit For This Useful Post:

    userjh160 (07-06-2019)

  13. Top | #7
    userjh160's Avatar
    Join Date
    Aug 2015
    Last Online
    Today @ 01:00 PM
    Location
    North Louisiana
    Posts
    324
    Thanks
    158
    Thanked 50 Times in 23 Posts
    Awesome, looks like its unanimous. It's great to have a friendly knowledgable forum to turn to. Thank y'all very much.

    Sent from my SM-G930V using Tapatalk
    Gizmo2, jimmylh and Toughsox like this.
    2017 3038E; RC2048, 4' Box Blade, Forks, 5' Rear Blade, 2017 Z920M

  14. Top | #8
    userjh160's Avatar
    Join Date
    Aug 2015
    Last Online
    Today @ 01:00 PM
    Location
    North Louisiana
    Posts
    324
    Thanks
    158
    Thanked 50 Times in 23 Posts
    Oh and I absolutely will NOT be doing this myself. My skills dont extend any further than replacing a light switch.

    Sent from my SM-G930V using Tapatalk
    Kennyd, Gizmo2, Toughsox and 1 others like this.
    2017 3038E; RC2048, 4' Box Blade, Forks, 5' Rear Blade, 2017 Z920M

  15. Top | #9

    Join Date
    Mar 2019
    Last Online
    Today @ 08:53 AM
    Location
    Northeast SD
    Posts
    417
    Thanks
    57
    Thanked 36 Times in 26 Posts
    Quote Originally Posted by userjh160 View Post
    Oh and I absolutely will NOT be doing this myself. My skills dont extend any further than replacing a light switch.

    Sent from my SM-G930V using Tapatalk
    Very wise indeed.
    One of the potential pitfalls is that incorrect oftentimes functions as normal and may not be realized until a tragedy has occurred.

  16. Top | #10
    IndianaJim's Avatar
    Join Date
    Feb 2013
    Last Online
    09-16-2019 @ 06:08 PM
    Location
    Indiana
    Posts
    1,448
    Thanks
    24
    Thanked 198 Times in 151 Posts
    Well, quite a bit depends on a lot of factors.

    How much power do you want in your shop? How many amps...

    How much is available from your house panel?
    ---How many amps is your house panel rated for?

    How big is your current meter base? How many amps...
    ---You might be able to come off the base with a disconnect and run to a subpanel in the garage if you have the available capacity to do so.
    If not, you may be able to upgrade the meter base to be able to accomplish this.
    This is likely your best option.

    I would recommend running 100 amps for any future requirements you might have, and on a separate circuit from the house panel, IE subpanel.

    The rest of this gets fairly windy.

    Years ago in our old house, I had a single 20 amp breaker going to my garage.
    That was fine for the odd one man project and little air compressor I had, but adding a Hobart Handler 140 115V welder was too much.
    I decided to upgrade, and after looking at everything, I added a double pole 60 amp breaker to the house panel and ran a trench with wire to the garage and added a sub panel there.
    It worked fine even when I upgraded to a 220V Handler 187 and added a Hypertherm Powermax 45.

    Fast forward a few years to moving to a new place.
    Similar issue, except I had 30 amps and a subpanel already.

    The trouble I had though was that the house had two 200 amp meter bases, and two 100 amp panels. They were fairly maxed out, so no room to expand without getting creative.
    I was going to run a sub off of one of the meter bases, but after checking with the power company, I found out the supply to the house wasnt rated to accept any more that was already on it.
    That changed the plans significantly.

    Our local power company did some calculations, and figured that if I wanted 200 amp service to the shop, they could run the wire from the existing transformer and install the meter at my cost, or I could let them run new wire to the house, to a 400 amp meter base, and they wouldnt charge me a penny.
    Thats what I did.
    I then added 3 exterior disconnects, one for each panel, per local code.
    One for each interior panel in the house, and one for the garage.
    All 100 amps.
    I could have gone bigger, but there was no point.
    I trenched from the house to the garage, ran 2ga wire and installed the 100 amp panel there with more than enough circuits to do anything I need now and might want in the future.
    I did all this work myself, including all wiring, box installs etc, except the work the power company did running the wire and attaching it to my 400 amp meter base.
    From that meter base, everything else was my responsibility.
    Interestingly enough, where I live there are no inspectors, and while Im plenty confident in my abilities, I know several people who do things like I do that arent nearly as capable or conscientious of safety requirements or codes.

    Anyway, its all been good for a few years now, although I do wish when I ran the trench and wire to the shop, Id have run a second trench with a gas line for a heater.
    Oh well. A project for another time I guess!
    Last edited by IndianaJim; 07-07-2019 at 01:04 PM.
    Toughsox likes this.
    Jim B.

    318, 49 Thrower, 2 80 Carts, 17AT cart, 54 Blade, 12" Brinly Plow, 30 Hydraulic Tiller w/extension & Briney 3-Pt hitch, 50 deck w/JRCO Cart Bagger.
    2025R, 120R loader w/Kens Bolt On Hooks, 260B backhoe w/8" & 16" buckets, Titan 36" forks, Imatch hitch, Weight Bracket/Hitch.

    Exmark Lazer Z HP 52"
    Husqvarna 550XP, 562XP, 55 Rancher

  17. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •