    Pole Barn Electric Run

    I have a 36 x 32 Pole barn with second story. I plan on running electric, water and cable to the barn. It is about a 75' run from the Main panel in the house to the barn. I plan on putting in a 100 amp service. All services will be split off the service I already have at the house (sub-panel off my main panel for barn). My questions are the following:

    What size/type wire should I use?

    Would it be better to run a seperate service from the pole rather than the house? Run to pole would be about 300 feet.

    Any other ideas or recommendations would be appreciated.

    Kennyd gave me his version and will add more to this thread. Thanks Kenny.
    2005 New Holland TC33DA Tractor
    FEL W/60" Bucket
    757 Backhoe/18"
    5' Box blade
    48" Pallet Forks
    Receiver for 3PT Hitch

    2012 John Deere 1026R
    60" MMM/Independent Hydraulic Lift
    Bagger System
    54" Quick Attach front plow

    All Stihl Power Equipment; FS 76 Brush Cutter, 044 Chain Saw

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2
    Senior GTT Super Slacker Gizmo2's Avatar
    Join Date
    Jan 2011
    Last Online
    Today @ 08:36 AM
    Location
    New York
    Posts
    34,191
    Thanks
    5,769
    Thanked 3,951 Times in 2,913 Posts
    I would run off the house and save the basic service charge. I would also have a local electric company give you a quote to provide all materials, run the wire and hook up the new panel.
    We did our garage last year and for the cost of an electrician that basically shows up with an electrical wholesale company on wheels it ends up being a couple hour job. I gave the company 8 hours of work to be fair and had the guy help with other wiring in the garage until he had a full day. $1,000.00 done deal. My wife and I installed the conduit from the house to the garage. Electrical run was about 80 ft.
    Keith

    JD 2320, 200CX FEL/61" bucket , 46 BH/16" bucket, Artillian Forks, 72" Snow Blade, Landscape Rake, Ballast Box, PHD, The Wife
    BX42 Chipper, XUV 560 Gator, Z915B ZTrak

  4. Top | #3
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 08:33 AM
    Location
    Westminster, MD
    Posts
    16,254
    Thanks
    4,995
    Thanked 4,035 Times in 2,514 Posts
    My answer to the PM:
    Bob, Mine is setup as a 100 amp subpanel off of my main, it's feed by three #2 AL conductors one #6 copper for the ground. The run is about 75'. I used what's called URD triplex cable rated for direct burial although I placed it into 2" conduit.

    Here is an example: http://products.customwireandcable.c...-direct-burial


    There are other types of wire you can use, but I got a "deal" on this stuff so that's what I used.
    Are you going to do this yourself?
    What size main panel do you have and how many spaces are blank?
    Is a path/conduit already installed?
    Do you understand that you need 4 conductors and keep your grounds and neutrals separated in the subpanel?
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    Lebneh's Avatar
    Join Date
    Oct 2011
    Last Online
    03-11-2019 @ 10:18 PM
    Location
    North East
    Posts
    26
    Thanks
    1
    Thanked 1 Time in 1 Post
    I did something similar. I ran from the house to the shed underground.


    You might think about running some Internet line as well(cat 5e or 6 should be plenty for basic needs). That way if you ever want to take advantage of Ethernet you don't have to dig up the ground again. Just make sure to get shielded cable if it's going to be near the power line.
    ~Lebneh

  7. Top | #5
    arlen's Avatar
    Join Date
    Apr 2012
    Last Online
    Today @ 08:00 AM
    Location
    South East Minnesota
    Posts
    3,145
    Thanks
    334
    Thanked 416 Times in 314 Posts
    Quote Originally Posted by Kennyd View Post
    My answer to the PM:



    Do you understand that you need 4 conductors and keep your grounds and neutrals separated in the subpanel?
    Kenny is warning you of a very common pit fall.
    I'll warn you of a couple more.
    1) You will need to drive a ground rod, and if you are pouring concrete with rebar, you have to tie your grounding electrode conductor to that as well.
    2) Make sure your URD actually carries a dual rating of USE as well. All modern URD does, but if you have some laying around, check to make sure.
    3) Make sure you use schedule 80 PVC conduit where you are emerging from the ground.
    4) Direct burial cables need 24 inches of cover.
    5) You need a warning ribbon 12 inches (or so) above the wires.
    6) Snake the wire back and forth a little in the trench and put a gentle"s" curve in in the wires at the ends to allow for ground movement and thermal expansion.
    7) Penetrate your conduits on each end of the run into the ground at least 18"
    8) Use a bushing on the ends of the conduits to protect the wires.
    9) make sure you line your trench with nice black dirt, clay, or sand. Then cover with the same; NO ROCKS.
    10) check with your inspector regarding using #2 AL to a building. The NEC allows this for dwelling units only. Many inspectors allow #2, but some do not. You may have to use #1 AL (see NEC table 310.15 (B) (7))
    11) Check with your inspector regarding your trench. If you explain to him how you plan on doing it, he may tell you it's OK to cover it up before he sees it. This is very handy if you are working on weekends.
    12) Check with your inspector with everything. They don't mind and it will save you some headaches. Remember, even when they are wrong, they are right
    13) clean the AL wires up good with a stainless steel brush, and work some anti oxidant goop into the wires before you terminate.
    14) Don't nick the wire when you strip it; AL hates this.
    15) make sure if you go under driveways or slabs, you are in conduit.
    Good luck, it's not hard.
    All this stuff is in the code except 13. I can give you the code references if you want them.
    4720 66hp Open Station, Power Beyond, 3rd, 4th and 5th Rear SCV, iMatch, 400cx with SSQA, 3rd Loader Function, MX6, BoDozer Grapple
    JD 320D Skid Loader
    Gator 865r...Fully Pimped Out

    X748SE 24hp, 647 Tiller, 54" front blade, 47 Snow Blower, 62C deck, JD disk

    JD 997 Zero Turn

    Farmall B

    2 miniature donkeys, 1/8 hp (each)

  8. The Following 2 Users Say Thank You to arlen For This Useful Post:

    Kennyd (08-15-2012), rgd (08-14-2012)

  9. Top | #6
    Martian's Avatar
    Join Date
    Mar 2012
    Last Online
    06-24-2013 @ 11:25 AM
    Location
    Flint, MI
    Posts
    792
    Thanks
    13
    Thanked 60 Times in 48 Posts
    Quote Originally Posted by arlen View Post
    Kenny is warning you of a very common pit fall.
    I'll warn you of a couple more.
    1) You will need to drive a ground rod, and if you are pouring concrete with rebar, you have to tie your grounding electrode conductor to that as well.
    2) Make sure your URD actually carries a dual rating of USE as well. All modern URD does, but if you have some laying around, check to make sure.
    3) Make sure you use schedule 80 PVC conduit where you are emerging from the ground.
    4) Direct burial cables need 24 inches of cover.
    5) You need a warning ribbon 12 inches (or so) above the wires.
    6) Snake the wire back and forth a little in the trench and put a gentle"s" curve in in the wires at the ends to allow for ground movement and thermal expansion.
    7) Penetrate your conduits on each end of the run into the ground at least 18"
    8) Use a bushing on the ends of the conduits to protect the wires.
    9) make sure you line your trench with nice black dirt, clay, or sand. Then cover with the same; NO ROCKS.
    10) check with your inspector regarding using #2 AL to a building. The NEC allows this for dwelling units only. Many inspectors allow #2, but some do not. You may have to use #1 AL (see NEC table 310.15 (B) (7))
    11) Check with your inspector regarding your trench. If you explain to him how you plan on doing it, he may tell you it's OK to cover it up before he sees it. This is very handy if you are working on weekends.
    12) Check with your inspector with everything. They don't mind and it will save you some headaches. Remember, even when they are wrong, they are right
    13) clean the AL wires up good with a stainless steel brush, and work some anti oxidant goop into the wires before you terminate.
    14) Don't nick the wire when you strip it; AL hates this.
    15) make sure if you go under driveways or slabs, you are in conduit.
    Good luck, it's not hard.
    All this stuff is in the code except 13. I can give you the code references if you want them.
    Electricity is one thing I will never understand, I'm just glad there are smart people like you that can figure it out
    2005 Deere 110 TLB - 3rd function loader, 3 rear remotes, thumb, top n tilt
    2000 Deere 5410 - 541 SL loader, 2 rear remotes, canopy
    2005 Deere Diesel HPX Gator - homemade cab, snow plow, hydraulic dump
    1953 Farmall Cub - front plow
    1984 Ford F8000 - Cat 3208 Diesel, 5+2 transmission, 8 yard dump
    2006 GMC 4500 Topkick Pickup outfitted by Monroe Truck

    Everyone has a fair turn to be as great as he pleases - Jeremy Collier

  10. Top | #7
    arlen's Avatar
    Join Date
    Apr 2012
    Last Online
    Today @ 08:00 AM
    Location
    South East Minnesota
    Posts
    3,145
    Thanks
    334
    Thanked 416 Times in 314 Posts
    Quote Originally Posted by Martian View Post
    Electricity is one thing I will never understand, I'm just glad there are smart people like you that can figure it out
    Thanks for the kind words. One thing I've learned from this forum: With the incredible diversity of all of us, together we make a pretty smart guy
    This forum is better than google
    4720 66hp Open Station, Power Beyond, 3rd, 4th and 5th Rear SCV, iMatch, 400cx with SSQA, 3rd Loader Function, MX6, BoDozer Grapple
    JD 320D Skid Loader
    Gator 865r...Fully Pimped Out

    X748SE 24hp, 647 Tiller, 54" front blade, 47 Snow Blower, 62C deck, JD disk

    JD 997 Zero Turn

    Farmall B

    2 miniature donkeys, 1/8 hp (each)

  11. Top | #8

    Join Date
    Jun 2012
    Last Online
    03-14-2016 @ 10:15 AM
    Location
    North Carolina
    Posts
    43
    Thanks
    0
    Thanked 5 Times in 5 Posts
    300ft will be a long run for CAT 5 cable, that's at the max range for ethernet. Just something to keep in mind.
    Matt

    John Deere 1026 R
    RC2048 Rotary Cutter
    Land Pride 54" Box Blade

  12. Top | #9
    Official "Groovie" Dude
    Join Date
    Jun 2011
    Last Online
    @
    Location
    N/A
    Posts
    5,663
    Thanks
    1,459
    Thanked 744 Times in 605 Posts
    I did mine the opposite, shed to house do to construction timing. One question I have is how many amp service did the utility hook you up to? I had a choice between 200 or 300 AMP service and went with the higher.

  13. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

Similar Threads

  1. 28'x40' Pole Barn Day one!...........
    By Scotty370 in forum Barns & Buildings
    Replies: 105
    Last Post: 05-20-2013, 07:22 AM
  2. pole barn
    By castiman in forum Barns & Buildings
    Replies: 15
    Last Post: 10-09-2012, 01:02 PM
  3. Insulating & sheeting inside a pole barn
    By castiman in forum Barns & Buildings
    Replies: 3
    Last Post: 09-10-2012, 06:37 PM
  4. OK some pic's of my pole barn
    By pcabe5 in forum Barns & Buildings
    Replies: 13
    Last Post: 01-15-2012, 09:57 AM
  5. How many of you guys run Biodiesel? B5 or B20
    By Brian in forum Large Frame Compact Utility Tractors (LCUT)
    Replies: 25
    Last Post: 11-03-2011, 06:00 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •