    Maintenance in long runs (generator)

    So we lost our power a couple days ago and we have a large PTO generator for our farm. I know the generator can run indefinitely but what should I check when running a tractor this long without a break at the same RPM. Maybe it doesn't matter and I'm pretty sure it doesn't but I thought I would ask. Thanks!

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2
    Pedals2Paddles's Avatar
    Join Date
    Jun 2018
    Last Online
    Today @ 07:58 PM
    Location
    MD
    Posts
    521
    Thanks
    10
    Thanked 96 Times in 50 Posts
    Well, you'll hit your every 200 hour service interval pretty soon, and then every 8 days thereafter.

    • Change engine oil and filter.
    • Change transmission oil and filter.
    • Clean transmission suction screen and internal magnets.
    • Check and service air filter elements. Check and service air filter elements when restriction indicator is red (1025R).
    • Clean radiator and oil cooler fins.
    • Inspect alternator belt.
    • Check wheel bolt torque.


    Then you have your every 400 hour service interval.

    • Replace air filter elements.
    • Replace fuel filters.


    If it were me, I'd be shutting it down to check the engine oil, hydraulic oil, air filters, radiator screen, and coolant levels every few days. And every time I refuel it, I would be eyeballing the coolant, radiator, and battery voltage. The continuous operation is probably less stressful than normal operation, but it's now critical infrastructure. A breakdown has much bigger implications than the grass growing too tall.

    Out of curiosity, how high do you have to have the throttle to meet your electrical load? What are you burning in fuel per hour?
    jdforever likes this.
    1025r | 60D | Forks | AV20F Grapple & 3rd SCV | 60" Box Blade | Danuser G20/40 Auger | Titan Pine Straw Rake | Kenny's hooks, springs, & diff lock pedal | LED Lighting Upgrades | HF Quick Hitch w/ extended top hook | Heavy Hitch weight bracket & toothbar | Custom loader snow plow


  4. Top | #3
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 07:41 PM
    Location
    Westminster, MD
    Posts
    16,269
    Thanks
    4,998
    Thanked 4,035 Times in 2,514 Posts
    Quote Originally Posted by Pedals2Paddles View Post
    Out of curiosity, how high do you have to have the throttle to meet your electrical load?
    PTO gensets have to run at 540 RPM so the frequency output is 60hz, so the tractor has to run at whatever RPM the 540 speed equates too.
    dieselshadow and jdforever like this.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    Keeper of the GTT Cookies dieselshadow's Avatar
    Join Date
    Nov 2011
    Last Online
    Today @ 09:29 PM
    Location
    Joelton TN
    Posts
    19,798
    Thanks
    1,065
    Thanked 4,296 Times in 2,584 Posts
    Quote Originally Posted by Kennyd View Post
    PTO gensets have to run at 540 RPM so the frequency output is 60hz, so the tractor has to run at whatever RPM the 540 speed equates too.
    Just to expand a bit.... The governor within the engine will try to maintain the RPM as the load increases. It will back off the fueling when the load drops.

    Tractors typically donít have the tightest governors like generator sets do. Gen sets have governors a lot more sensitive to RPMs. Most tractors will vary the RPM enough to have small fluctuations in frequency. But they are no worse than portable type generators.
    Kennyd and jdforever like this.
    - Jason

    GreenTractorTalk.com Rules, Policies, and Terms of Use

    Subscribe to dieselshadowman on YouTube

    2720 w/ 200CX FEL
    , Ken's weld-on hooks, Fit Rite Hydraulics Top and Tilt kit, Artillian forks.
    1954 60 - getting full restoration, 1964
    110 round fender in the shop for crustoration
    Ferris IS3200Zzero turn mower

  7. Top | #5
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 07:41 PM
    Location
    Westminster, MD
    Posts
    16,269
    Thanks
    4,998
    Thanked 4,035 Times in 2,514 Posts
    Quote Originally Posted by dieselshadow View Post
    Just to expand a bit.... The governor within the engine will try to maintain the RPM as the load increases. It will back off the fueling when the load drops.

    Tractors typically donít have the tightest governors like generator sets do. Gen sets have governors a lot more sensitive to RPMs. Most tractors will vary the RPM enough to have small fluctuations in frequency. But they are no worse than portable type generators.
    I'll even expand a bit more....

    It doesn't matter if you're running a night light or a heater, in other words a light or heavy load, you still ned to run at 540 to painted the correct voltage and frequency, this is especially tru with motors and electronics.


    But we are getting a bit off topic here. I would be checking the tractors fluids about every 4 hours or so.
    dieselshadow and jdforever like this.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  8. Top | #6

    Join Date
    Jul 2018
    Last Online
    Today @ 06:53 PM
    Location
    South Eastern, Connecticut
    Posts
    375
    Thanks
    3
    Thanked 48 Times in 43 Posts
    Quote Originally Posted by Pedals2Paddles View Post
    Well, you'll hit your every 200 hour service interval pretty soon, and then every 8 days thereafter.

    • Change engine oil and filter.
    • Change transmission oil and filter.
    • Clean transmission suction screen and internal magnets.
    • Check and service air filter elements. Check and service air filter elements when restriction indicator is red (1025R).
    • Clean radiator and oil cooler fins.
    • Inspect alternator belt.
    • Check wheel bolt torque.


    Then you have your every 400 hour service interval.

    • Replace air filter elements.
    • Replace fuel filters.


    If it were me, I'd be shutting it down to check the engine oil, hydraulic oil, air filters, radiator screen, and coolant levels every few days. And every time I refuel it, I would be eyeballing the coolant, radiator, and battery voltage. The continuous operation is probably less stressful than normal operation, but it's now critical infrastructure. A breakdown has much bigger implications than the grass growing too tall.

    Out of curiosity, how high do you have to have the throttle to meet your electrical load? What are you burning in fuel per hour?
    This says everything you need to do. You need to maintain your regular service intervals for the equipment. I've operated many a diesel genset both in continuous and intermittent duty cycles. The service intervals never really change it's all a matter of how quickly you get to them.

    Typically in smaller gensets with simple engine governors the no load RPM is set so that the generator outputs around 61-62Hz. At around 50% load the output frequency falls to around 60Hz. As you need max output the frequency falls to 59-58Hz.

    Above 62 and below 58 you really start to risk damage long term. Any time you are on backup power its always advisable to keep and eye on the frequency output of the generator. You can also infer engine load based of frequency if you don't have a watt meter.
    X738, 54HC deck w/ auto connect, 3PH
    Woods GBC48 box scraper
    Day dreaming of a 54" snow blower

  9. Top | #7
    Pedals2Paddles's Avatar
    Join Date
    Jun 2018
    Last Online
    Today @ 07:58 PM
    Location
    MD
    Posts
    521
    Thanks
    10
    Thanked 96 Times in 50 Posts
    Oh, I forgot to say... the hourly service I posted is from a 1-series. So adjust based on whatever machine you're using. But I can't imagine it being much different. Concept is the same I would thing. What tractor are you using for this?
    1025r | 60D | Forks | AV20F Grapple & 3rd SCV | 60" Box Blade | Danuser G20/40 Auger | Titan Pine Straw Rake | Kenny's hooks, springs, & diff lock pedal | LED Lighting Upgrades | HF Quick Hitch w/ extended top hook | Heavy Hitch weight bracket & toothbar | Custom loader snow plow


  10. Top | #8

    Join Date
    Apr 2019
    Last Online
    09-10-2019 @ 06:11 PM
    Posts
    54
    Thanks
    0
    Thanked 1 Time in 1 Post
    It's a 5083EN and I have been watching fluids and engine temps. It's running at.. 1600 I think for economy PTO. Very stable output and nice generator. Thanks for the information!

  11. Top | #9
    jgayman's Avatar
    Join Date
    Jul 2012
    Last Online
    Today @ 09:27 PM
    Location
    Central Pennsylvania
    Posts
    9,803
    Thanks
    368
    Thanked 1,610 Times in 1,223 Posts
    Quote Originally Posted by Shadow_storm56 View Post
    So we lost our power a couple days ago and we have a large PTO generator for our farm. I know the generator can run indefinitely but what should I check when running a tractor this long without a break at the same RPM. Maybe it doesn't matter and I'm pretty sure it doesn't but I thought I would ask. Thanks!
    This is probably the best argument for NOT using a tractor for long term emergency power. One year during a hurricane I powered my house for 4 days from my portable generator and didn't think twice about it.

    Having my tractor sitting out in the rain and wind for 4 days with the engine screaming wide open to maintain 540 RPM on the PTO doesn't sound like the best approach. :-)

    As for maintenance, is your tractor really going to be running THAT long? I mean, even if you go over the recommended hours for the maintenance interval it isn't going to blow up. And if per chance you find it just HAS to have an oil change during the outage, disconnect the load, shut down the tractor and service it. The fridge and freezer will be fine.
    2012 2720 -- 200CX Loader -- 54" Quick Attach Snow Blower -- Frontier LR5060 Rake -- Land Pride RB1660 Blade (Hydraulic Angle) -- Artillian 42" Forks -- Ken's Bolt on Grab Hooks -- Fit Rite Hydraulic top-link -- 2013 X500 for mowing duties

  12. Top | #10

    Join Date
    Mar 2015
    Last Online
    Today @ 09:27 PM
    Location
    Eastern Virginia, United States
    Posts
    4,491
    Thanks
    341
    Thanked 812 Times in 529 Posts

    What are you powering?

    Quote Originally Posted by jgayman View Post
    This is probably the best argument for NOT using a tractor for long term emergency power. One year during a hurricane I powered my house for 4 days from my portable generator and didn't think twice about it.

    Having my tractor sitting out in the rain and wind for 4 days with the engine screaming wide open to maintain 540 RPM on the PTO doesn't sound like the best approach. :-)

    As for maintenance, is your tractor really going to be running THAT long? I mean, even if you go over the recommended hours for the maintenance interval it isn't going to blow up. And if per chance you find it just HAS to have an oil change during the outage, disconnect the load, shut down the tractor and service it. The fridge and freezer will be fine.
    We've had some very long runs without power- 10-14 days with ice storms and hurricanes. It's the product of being at the tail end of the power line with no alternative feed. After the second time we went through that fun, I bought a whole house generator but even with that it gets shut down at night. So max run is about 18 hours/day for household use. I check the oil before restarting it in the mornings. With the portable generators, I changed the oil after a couple days of running.

    But if you are powering a dairy, or ventilation fans for confined animal facilities you don't have that luxury. In those cases, I'd check fluids every time I had to refuel. An extra couple of minutes won't matter but it could keep you from a serious issue.

    Treefarmer
    jdforever and ttazzman like this.
    John Deere 790, 300 loader w Ken's Bolt on Hooks & Piranha tooth bar, grapple, back blade, box blade, Bush Hog mower, couple of red tractors, hay equipment, various old stuff some red, one orange, some I don't remember