    any electricians around?

    looking to upgrade my panel from a 100amp service, and checked out the wire to see what I could get away with. turns out the cable says:

    KAISER KATHENE (UL) SPEC 400 AWG AL 500 VOLTS TYPE XHHW

    so, a little googlefu returned that this may be 400kcmil wiring, which is rated up to.... 280amps?! that can't be right? did I miss something here?

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2

    Join Date
    May 2017
    Last Online
    Today @ 01:09 PM
    Location
    Nw iowa
    Posts
    92
    Thanks
    1
    Thanked 6 Times in 6 Posts
    I can’t imagine that you have 400 kcmil wire connected to a 100 amp service....the lugs typically aren’t rated for that large of wire. I picture would really help a lot.
    Gizmo2 and lewisc1985 like this.
    2017 2038R, 220R loader, AF12 pallet forks, 6 60# wheel weights, ballast box, Dual Rear SCVs, Premium LED lighting kit

  4. Top | #3
    Herminator's Avatar
    Join Date
    Mar 2017
    Last Online
    Today @ 12:05 AM
    Location
    Northern Illinois
    Posts
    3,909
    Thanks
    1,728
    Thanked 841 Times in 630 Posts
    Wire Size Calculator

    There are a number of wire size calculator’s on google. It depends on the length of the run, how much voltage drop you can live with and if you are going to use copper or aluminum. Good luck. If you are gong to be welding off that feed I would go at least a size heavier in wire just because it helps keep the lights from dimming. If it is a long buried run I would double it. I should say I did double it. My shed has a 100amp service but I sized the wires for 200 just because I don’t want to do that again.
    Welcome to Intermission.

    2017 2038R, 400, 3020 & HPX and thingies to hook to the them.
    112 - Sold in July 2017 but took me until November to admit I just cast it out into this cruel world.
    #compactfarmer

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4

    Join Date
    Mar 2015
    Last Online
    01-26-2019 @ 12:01 AM
    Location
    finger lakes, ny
    Posts
    424
    Thanks
    7
    Thanked 45 Times in 38 Posts
    you know what, after moving all the wires out of the way to get a good shot of the wire... a very faint "2" that was half rubbed off became visible next to the AWG. 😭 this project just got more expensive.. and I may have to repaint and re-drywall....

  7. Top | #5
    flyweight's Avatar
    Join Date
    Jun 2014
    Last Online
    Today @ 10:08 AM
    Location
    Louisiana, (southeast)
    Posts
    9,363
    Thanks
    820
    Thanked 1,733 Times in 1,194 Posts
    You sure it's not 4/0 AL printed on the feed wire? A 200 AMP service uses 2/0 Copper, or 4/0 Aluminum(Aluminum Clad).

    Click image for larger version. 

Name:	wiresize.png 
Views:	18 
Size:	13.7 KB 
ID:	536546
    Gizmo2, pappa and nomorr1 like this.
    Michael

    2019 JD Z540R 54" cutting deck w/MulchControl™
    1984 JD 750
    1971 JD 15 Chainsaw ← hasn't run since ~1975

    Also have a bunch of other stuff.
    ---------------------------------------
    " If there's no one around to smell me, do I really stink"?
    - John Wells - Brewster County, West Texas.










  8. Top | #6

    Join Date
    Mar 2015
    Last Online
    01-26-2019 @ 12:01 AM
    Location
    finger lakes, ny
    Posts
    424
    Thanks
    7
    Thanked 45 Times in 38 Posts
    Quote Originally Posted by Herminator View Post
    Wire Size Calculator

    There are a number of wire size calculator’s on google. It depends on the length of the run, how much voltage drop you can live with and if you are going to use copper or aluminum. Good luck. If you are gong to be welding off that feed I would go at least a size heavier in wire just because it helps keep the lights from dimming. If it is a long buried run I would double it. I should say I did double it. My shed has a 100amp service but I sized the wires for 200 just because I don’t want to do that again.
    no tools on this drop, it's just a small cabin in the woods. the real upgrade is so that I can run a 24kw on demand water heater. the panel is located about 6 cable feet from the meter on the outside of the house, but it's tucked into a wall I just closed up about a year ago, getting this place habitable again

  9. Top | #7

    Join Date
    May 2017
    Last Online
    Today @ 01:09 PM
    Location
    Nw iowa
    Posts
    92
    Thanks
    1
    Thanked 6 Times in 6 Posts
    Quote Originally Posted by lewisc1985 View Post
    you know what, after moving all the wires out of the way to get a good shot of the wire... a very faint "2" that was half rubbed off became visible next to the AWG. 😭 this project just got more expensive.. and I may have to repaint and re-drywall....
    That size sounds better. Typically when I do a service change out the existing wires wouldn’t be long enough in the first place if they were the correct size. How long of wire run and type of service are you talking about? You would need to change the meter socket etc and bring the grounding and other parts of the system up to code in most cases too. Basically what I am getting at here is unless it is an unusually long run the wire cost isn’t that much different but each job is different.
    SulleyBear likes this.
    2017 2038R, 220R loader, AF12 pallet forks, 6 60# wheel weights, ballast box, Dual Rear SCVs, Premium LED lighting kit

  10. Top | #8

    Join Date
    Mar 2015
    Last Online
    01-26-2019 @ 12:01 AM
    Location
    finger lakes, ny
    Posts
    424
    Thanks
    7
    Thanked 45 Times in 38 Posts
    Quote Originally Posted by danselec07 View Post
    That size sounds better. Typically when I do a service change out the existing wires wouldn’t be long enough in the first place if they were the correct size. How long of wire run and type of service are you talking about? You would need to change the meter socket etc and bring the grounding and other parts of the system up to code in most cases too. Basically what I am getting at here is unless it is an unusually long run the wire cost isn’t that much different but each job is different.
    the run is seriously only about 6 feet from the meter to the panel. i'll probably go to 200amp service, just to futureproof a bit, but honestly, I was just hoping I could've popped a 150a breaker into the panel if the wire was that over sized... lazy lazy! haha

  11. Top | #9

    Join Date
    Jan 2012
    Last Online
    Today @ 11:45 AM
    Location
    East Central Indiana
    Posts
    1,468
    Thanks
    92
    Thanked 240 Times in 172 Posts
    Quote Originally Posted by lewisc1985 View Post
    the run is seriously only about 6 feet from the meter to the panel. i'll probably go to 200amp service, just to futureproof a bit, but honestly, I was just hoping I could've popped a 150a breaker into the panel if the wire was that over sized... lazy lazy! haha
    It is never a good idea to take shortcuts on an electrical panel. I have seen to many shortcuts taken over the years, that have cost current owners lots of money & risked the lives of lots of people.
    glc, Gizmo2, pappa and 3 others like this.
    Kioti CK3510SE HST, Kioti KL4030 Loader, John Deere 655 Tiller, Frontier LR2072 Landscape Rake, Virnig V50 Pallet Forks, Woods GB60 Box Blade
    John Deere X739 AWS 4X4, 60HC Auto Connect Deck, Front grader blade.
    John Deere 825i Gator

    John Deere Tractors I have owned in the past.
    425 AWS, 455, 4400, 2210, 4710, 2320, 2720, X475, 1026R, 4120, 2025R

  12. Top | #10
    pappa's Avatar
    Join Date
    Mar 2013
    Last Online
    Today @ 10:46 AM
    Location
    State of Jefferson
    Posts
    4,979
    Thanks
    242
    Thanked 437 Times in 346 Posts
    Quote Originally Posted by lewisc1985 View Post
    the run is seriously only about 6 feet from the meter to the panel. i'll probably go to 200amp service, just to futureproof a bit, but honestly, I was just hoping I could've popped a 150a breaker into the panel if the wire was that over sized... lazy lazy! haha
    How far is the transformer from the service panel and what size wire did the power company use. It may have to be upsized also!
    2320 200cx loader, 46 backhoe, 54"snowblower, original cab, Titan 42" forks, welded on hooks by neighbor.