    Sharing a circuit for AC and welder

    I am exploring options for adding a welder outlet to my garage and would appreciate any advice you might have.


    My garage panel has no open breaker slots and is set up with only one 230V/20a circuit that is hardwired to the mini-split AC unit. I was wondering if it is safe/legal to run a line from that breaker to a SPDT (on-off-on) switch that could be used to select between the existing AC circuit OR a new 20a welder outlet, but never both at the same time.

    Here is the switch:

    https://www.homedepot.com/p/Leviton-...1287/301447054

    The welder (Lincoln 210MP) shows a draw of 14.7 amps, so a 20a breaker should be OK.

    All wiring would be matched 12-2 and the current 20a breaker protection would be maintained.

    Thanks!

    Mike

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2

    Join Date
    Jun 2014
    Last Online
    Today @ 09:58 PM
    Location
    Berlin, MA
    Posts
    4,596
    Thanks
    94
    Thanked 866 Times in 661 Posts
    It'd probably be easier to put in a small subpanel and replace your existing 20-amp breaker with a 50-amp breaker to feed the subpanel. Then just put 2 20-amp breakers in the subpanel and feed the A/C unit from one and the welder outlet from the other. T

    hen you could run both at the same time if you wanted to. You'd never have to mess with any switches or worry about forgetting something.
    D160 Mower/Bagger.
    2014 2032R tractor/H130 FEL w/Bolt-On Hooks/54" Snow Plow/iMatch Quick-Hitch/County Line 5' Scraper blade/County Line Carry-All/Artillian 42" Forks & QH Adapter/JD Ballast Box/Frontier SB1164 3PH Blower/Leinbach PHD/Wallenstien BX42 Chipper

  4. Top | #3
    Keeper of the GTT Cookies dieselshadow's Avatar
    Join Date
    Nov 2011
    Last Online
    Today @ 05:39 PM
    Location
    Joelton TN
    Posts
    19,772
    Thanks
    1,065
    Thanked 4,287 Times in 2,579 Posts
    I like Jimís idea, but its the most expensive option.

    Itís perfectly ok to daisy-chain another outlet on that circuit, but you will run the risk of tripping the breaker if you run both. You could simply add a switch (like a light switch) for the AC to shut it off or just use the remote and turn it off when you want to use the secondary outlet.

    I personally wouldnít get carried away with a two-way selector switch for this. Itís massively overkill. (So secretly I like it. LOL )
    mjncad, arlen, rtgt and 1 others like this.
    - Jason

    GreenTractorTalk.com Rules, Policies, and Terms of Use

    Subscribe to dieselshadowman on YouTube

    2720 w/ 200CX FEL
    , Ken's weld-on hooks, Fit Rite Hydraulics Top and Tilt kit, Artillian forks.
    1954 60 - getting full restoration, 1964
    110 round fender in the shop for crustoration
    Ferris IS3200Zzero turn mower

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    ttazzman's Avatar
    Join Date
    Feb 2019
    Last Online
    Today @ 10:10 PM
    Location
    sw mo
    Posts
    487
    Thanks
    18
    Thanked 64 Times in 49 Posts
    I would do what JimR outlined......i would probably just go ahead and do a 100amp (common and cheap) sub panel for possible future ussage since your out of breaker slots......

    the switch you linked to is a single pole switch i am not aware of a double pole switch (220v) like you want and you would require 12/3 wire not 12/2 for 220v ....unless i missed something...obviously the sub panel would need the correct wire size feeder

    a sub panel would probably cost less than the double pole switch if could even find one something like this with breakers and all https://www.homedepot.com/p/Square-D...PCVP/204836397
    Last edited by ttazzman; 04-13-2019 at 09:22 AM.
    mjncad, Tomfive and rtgt like this.
    John Deere
    5105M
    2140
    4500
    Caterpillar
    D4Hxl
    416C
    Gehl
    5635DX

  7. Top | #5
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 08:29 PM
    Location
    Westminster, MD
    Posts
    16,240
    Thanks
    4,992
    Thanked 4,030 Times in 2,510 Posts
    What panel do you have?
    In some you can add in some tandem breakers on a few 125v circuits to gain some space for another double breaker.
    Tomfive, ejb69, arlen and 6 others like this.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  8. Top | #6

    Join Date
    Mar 2019
    Last Online
    Today @ 07:00 PM
    Posts
    113
    Thanks
    0
    Thanked 6 Times in 3 Posts
    ^^^^^^

    It's a Siemens 1212 with a 40a main. Tandem breakers are a no-go

    The buried feed wire from the house appears to be aluminum and the conductors measure approximately .175. Based on that, I'm guessing 6ga which can't really support much more than the 40a main.
    Last edited by MN3046; 04-13-2019 at 09:29 AM.
    rtgt and JD4044M like this.

  9. Top | #7

    Join Date
    Mar 2019
    Last Online
    Today @ 07:00 PM
    Posts
    113
    Thanks
    0
    Thanked 6 Times in 3 Posts
    Quote Originally Posted by ttazzman View Post
    the switch you linked to is a single pole switch i am not aware of a double pole switch (220v) like you want and you would require 12/3 wire not 12/2 for 220v ....unless i missed something...obviously the sub panel would need the correct wire size feeder
    I believe a SPDT is the correct switch as this application has only a single "line" and two loads. I am referring to NM 12/2 + ground(3 conductors total). That is what is on the AC circuit now.

  10. Top | #8
    Tomfive's Avatar
    Join Date
    Dec 2011
    Last Online
    Today @ 10:17 PM
    Location
    Mid-Hudson Valley, NY
    Posts
    4,146
    Thanks
    97
    Thanked 605 Times in 470 Posts
    I agree with adding a subpanel, but don't skimp with a small (like a 6 breaker) panel, go for something with more spaces. My main panel has been space challenged for many years. As a temporary measure I put a couple of tandems in, though they are not approved for my panel. Then I put in a small 6 space panel for a few shop tools. It was handy, but then when I needed more I ended up replacing the small panel with a full sized 24 space one and fed it with a 100A breaker. No more illegal tandems and plenty of spare spaces for expansion.

    Just my 2 cents.
    mjncad, rtgt and JD4044M like this.
    Tom

    2011 1026R/R4's -- H120 FEL/49" -- 260 BH/12" -- Bro-Tek Ripper -- Artillian Forks/42" -- 244 lbs JD Rear Wheel Weights -- KBOH Hooks and Clevis' --
    Block heater -- 180* T-stat -- Evans HP Waterless Coolant

  11. Top | #9

    Join Date
    Mar 2019
    Last Online
    Today @ 07:00 PM
    Posts
    113
    Thanks
    0
    Thanked 6 Times in 3 Posts
    ^^^^^^

    That would be nice, but I only have 40a total available in that garage.
    rtgt likes this.

  12. Top | #10
    ttazzman's Avatar
    Join Date
    Feb 2019
    Last Online
    Today @ 10:10 PM
    Location
    sw mo
    Posts
    487
    Thanks
    18
    Thanked 64 Times in 49 Posts
    Quote Originally Posted by MN3046 View Post
    ^^^^^^

    It's a Siemens 1212 with a 40a main. Tandem breakers are a no-go

    The buried feed wire from the house appears to be aluminum and the conductors measure approximately .175. Based on that, I'm guessing 6ga which can't really support much more than the 40a main.

    you might do more checking ...i dont think they make a Aluminum (direct burried) UF-B wire....so if its aluminum its probably in a conduit and thus is replaceable should you wish to upsize it...

    FWIW..........175 is probably 6ga (.168) ......6ga aluminum's ampicity is 50amp ....it may be oversized for the 40amps for voltage drop due to length of the feeder...........6ga COPPER direct burried UF-B wire's ampicity is 55amps

    UF-B is the romex type wire that can be directly buried in the ground without conduit and is typically grey in color
    Last edited by ttazzman; 04-13-2019 at 09:52 AM.
    rtgt likes this.
    John Deere
    5105M
    2140
    4500
    Caterpillar
    D4Hxl
    416C
    Gehl
    5635DX

  13. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

Page 1 of 7 1 2 3 ... LastLast

Similar Threads

  1. Sharing: Hydraulic dump MCS on Baltimore CL
    By JAllen in forum For Sale
    Replies: 5
    Last Post: 11-21-2018, 10:54 PM
  2. Restoration compressor and welder
    By fdmars in forum Tools & Equipment
    Replies: 15
    Last Post: 12-31-2016, 01:11 PM
  3. 3320 and 3033R Cab: Underpowered under load with AC running or adequate?
    By jermedic in forum Large Frame Compact Utility Tractors (LCUT)
    Replies: 6
    Last Post: 02-18-2016, 11:17 PM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts