    Outlet Amperage/Wiring

    I have a Hobart 140 welder. The outlet it plugs into is a 14 gauge wire on a 15 amp breaker. As you can guess, I have blown the breaker a few times. I know the breaker needs to be changed to a 20 amp, but what about the wiring? I am thinking about changing it to 12 gauge, but one guy said it would not hurt to go to 10 gauge. Any thoughts?
    John Wayne, Jonny Cash & John Deere

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 03:50 PM
    Location
    Westminster, MD
    Posts
    16,569
    Thanks
    5,136
    Thanked 4,132 Times in 2,575 Posts
    If the outlet is fed by #14 wire, then you can NOT upgrade the breaker to a 20A. You must upgrade the wire to #12 also. The only advantage #10 would give is less voltage drop if it's a really long run from the panel.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  4. Top | #3
    eepete's Avatar
    Join Date
    Aug 2010
    Last Online
    05-26-2019 @ 06:02 PM
    Location
    Efland, NC 54 Acres, hay, ponds, woods.
    Posts
    971
    Thanks
    20
    Thanked 54 Times in 47 Posts
    Kennyd is right (as always).

    If you're going to put in new wire, think about putting in "the last wire you'll ever need for welding" which might be a 8-3 with ground? (welders chime in) Then you can go 240 40A at some point in the future. Just wire up a 20 amp 120 for now.

    Unless the run is longer that 100' (SWAG) then going to a #10 won't get you much. Only "exception" to that is if your 120V is normally a bit low (say 115 or less), in which case the #10 would be good since you're starting out a little low to begin with. I have the opposite problem here, I normally run about 125 volts all the time.

    Pete
    '09 JD4520 Cab (60HP), '97 KubotaB21 TLB (21HP), 400cx loader, MX6 rotary mower, SB1106 6' Sickle Bar, BB3272 6' box blade, GradeMaster 7' Landplane, Frontier AF11E Front Blade, 4' Pallet Forks, 6' landscape rake, ballast box, Woods GTC 40" tiller, PHD 9" auger, 4' x 8' chain harrow, '16 X755 (23HP Diesel) w/front PTO, 60" deck, 72" front blade, '90 JD318 (18HP gas) with 48" MM mower, 54" front blade, 47" snowblower.
    Volunteer Firefighter.

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    Captain Hook Kennyd's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 03:50 PM
    Location
    Westminster, MD
    Posts
    16,569
    Thanks
    5,136
    Thanked 4,132 Times in 2,575 Posts
    Quote Originally Posted by eepete View Post
    If you're going to put in new wire, think about putting in "the last wire you'll ever need for welding" which might be a 8-3 with ground? (welders chime in) Then you can go 240 40A at some point in the future.
    The "standard" welder outlet is wired with #8 wire, a 50 amp breaker, and a NEMA 6-50R ("R" is for receptacle). Most 220v welders come equipped with a 6-50P ("P" is for plug)

    The wire size can be de-rated slightly based on the duty cycle of the welder, that is why #8 can be used rather than #6 for 50 amps. Some even say you can use #10 wire but that is cutting it to close for my comfort level.
    Kenny

    -John Deere 3720 Deluxe Cab TLB
    FEL, MMM, Artillian 42" Forks and Modular Grapple, I-Match, Ballast Box, and lots of other STUFF.
    -John Deere 455 w/60" MMM


    Bolt on Grab Hooks and other cool stuff are now for sale!!

    Visit our YouTube Channel

    My Equipment:
    John Deere 3720 Deluxe Cab, 300cx FEL, 366 Front Blade, 59" Front Snowblower, Ballast Box
    Artillian 3K Forks, Grapple, Front-Hoe Bucket
    John Deere 455, 60" MMM

  7. Top | #5
    FordGuy's Avatar
    Join Date
    Sep 2010
    Last Online
    01-12-2011 @ 12:20 PM
    Location
    OHIO
    Posts
    157
    Thanks
    0
    Thanked 0 Times in 0 Posts
    Thanks, Its only a 20 foot run from the breaker. This old barn is not fun to work in. I thought some were being way overkill.
    John Wayne, Jonny Cash & John Deere

  8. Top | #6
    eepete's Avatar
    Join Date
    Aug 2010
    Last Online
    05-26-2019 @ 06:02 PM
    Location
    Efland, NC 54 Acres, hay, ponds, woods.
    Posts
    971
    Thanks
    20
    Thanked 54 Times in 47 Posts
    Oh. A few more post and we could of had buss bar running around your shop.

    At 20 feet, wire cost is irrelevant it comes down to your time. Glad it's an easy fix.

    Pete
    '09 JD4520 Cab (60HP), '97 KubotaB21 TLB (21HP), 400cx loader, MX6 rotary mower, SB1106 6' Sickle Bar, BB3272 6' box blade, GradeMaster 7' Landplane, Frontier AF11E Front Blade, 4' Pallet Forks, 6' landscape rake, ballast box, Woods GTC 40" tiller, PHD 9" auger, 4' x 8' chain harrow, '16 X755 (23HP Diesel) w/front PTO, 60" deck, 72" front blade, '90 JD318 (18HP gas) with 48" MM mower, 54" front blade, 47" snowblower.
    Volunteer Firefighter.

  9. Top | #7
    mjncad's Avatar
    Join Date
    Aug 2010
    Last Online
    Today @ 02:43 AM
    Location
    Front Range of Colorado
    Posts
    7,049
    Thanks
    1,815
    Thanked 557 Times in 442 Posts
    FG:

    Go with Kenny and Pete's advice. As I recall, I went with #8 when #10 would do; but I had a ~50' run and the cost differential between #8 and #10 wasn't enough to justify being cheap.
    I have more ideas than ambition.


  10. Top | #8

    Join Date
    Aug 2010
    Last Online
    10-31-2011 @ 03:39 PM
    Posts
    733
    Thanks
    0
    Thanked 4 Times in 4 Posts
    Quote Originally Posted by Kennyd View Post
    The "standard" welder outlet is wired with #8 wire, a 50 amp breaker, and a NEMA 6-50R ("R" is for receptacle). Most 220v welders come equipped with a 6-50P ("P" is for plug)

    The wire size can be de-rated slightly based on the duty cycle of the welder, that is why #8 can be used rather than #6 for 50 amps. Some even say you can use #10 wire but that is cutting it to close for my comfort level.
    I'm no electrician...BUT...While I agree that the 6-50R is the correct Plug, I'd say 8ga wire is not for 50A...50A = 6 Ga wire...

    I wired my garage with a NEMA 14-50R, gives me a neutral to get 110v 50A I made a 3' Cord with a box which has a 6-50R and a 5-20R
    Why did I do that? Couple reasons...
    -In the cut off pile at Lowes they had 60' of 6-3 Wire on clearance for 30 bucks..might as well use all the conductors at that point.
    -My shiny new (at the time) Dewalt Chop saw would CONSTANTLY trip the breaker, googling it showed it was common on that model saw and people had to wire 30A to run the saw...
    -My Welder outlet doubles as a generator hookup..Yes i know the dangers of not having an interlock.

    As for derating the wire based on duty cycle, I was taught that yes you can do that, only if its hardwired in. IF a recepticle is in, you should wire the "hard side" to match the breaker. Whats to prevent someone from coming in and hooking up a huge honkin 220v 50A heater to that outlet when your not around?

  11. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

Similar Threads

  1. Help pls - 1026R forward auxiliary light kit wiring
    By kimqi in forum Sub Compact Utility Tractors (SCUT)
    Replies: 22
    Last Post: 12-14-2014, 01:31 PM
  2. Electrical Wiring
    By Acolar in forum Large Frame Compact Utility Tractors (LCUT)
    Replies: 3
    Last Post: 11-22-2011, 09:15 AM
  3. rear wiring for lights
    By jruffner in forum Sub Compact Utility Tractors (SCUT)
    Replies: 5
    Last Post: 10-13-2011, 05:51 PM
  4. Wiring Schematics for LA105
    By strutsnbucks in forum Lawn & Garden Tractors
    Replies: 1
    Last Post: 06-06-2011, 01:03 PM
  5. Workshop Bench Outlet Strip Options
    By Aaron in forum Home & Workshop Projects
    Replies: 5
    Last Post: 02-24-2011, 08:57 AM

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •