    ? about Roxul nsulation and a fireplace insert chimney exhaust

    We bought a house that has a wood burning fireplace insert where a regular fireplace used to be. There is a strong cold draft that flows into the room around the insert. I believe most of the cold air is flowing down the chimney around the stainless steel exhaust tube running up the shaft. I want to try and seal the void around the exhaust tube. There is no live flame associated with the insert outside its chamber just the smoke and some heat. Can I use Roxul around the stainless exhaust pipe to pack and seal the void between the chimney and the tube?
    2014- JD 1025r
    L120 59" FEL, 260 BH, 60D MMM
    66"/54" plow with Artillian extension and rubber edge
    Artillian 36" forks
    JD 550 3PT Tiller
    54" spike aerator
    Fimco 3PT 40 gal boom sprayer
    Trac-Vac 580
    CMP 3PT 60" Dethatcher
    51" Lucknow 3PT rear snowblower
    Omni Transformer 3PT weight rack w/ 2" hitch receiver 6-42lbs weights

  2. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  3. Top | #2

    Join Date
    Dec 2016
    Last Online
    Yesterday @ 08:44 PM
    Location
    Michigan
    Posts
    156
    Thanks
    1
    Thanked 25 Times in 19 Posts
    Yes you can Roxul or any mineral wool type insulation will be fine. Don't use fiberglass home insulation.
    Ron

  4. Top | #3

    Join Date
    Jul 2015
    Last Online
    Yesterday @ 11:42 PM
    Location
    Near Roa. VA
    Posts
    3,537
    Thanks
    43
    Thanked 432 Times in 333 Posts
    I have used fiberglass for this type thing.

    To get a perfect answer,, you probably should ask Roxul.

    I have two fireplace chimneys' that are no longer used.
    I fabbed a cap for both of them from metal roofing,,


    The sealing helped keep the house cooleer in the summer,,,
    and warmer in the winter.

    With the metal roofing in place, the chimneys are no longer weather degrading,,
    another plus.

  5. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

  6. Top | #4
    96PSD's Avatar
    Join Date
    Jul 2014
    Last Online
    08-07-2019 @ 09:34 PM
    Location
    East Windsor, NJ
    Posts
    444
    Thanks
    15
    Thanked 60 Times in 43 Posts
    I use the insert from time to time during the winter to heat the first floor additionally. I did cap the rest of the chimney at the top around the exhaust pipe, but the chimney is about 25' tall and exterior to the house. So a lot of cold still infiltrates down on all that exterior exposed brick.
    2014- JD 1025r
    L120 59" FEL, 260 BH, 60D MMM
    66"/54" plow with Artillian extension and rubber edge
    Artillian 36" forks
    JD 550 3PT Tiller
    54" spike aerator
    Fimco 3PT 40 gal boom sprayer
    Trac-Vac 580
    CMP 3PT 60" Dethatcher
    51" Lucknow 3PT rear snowblower
    Omni Transformer 3PT weight rack w/ 2" hitch receiver 6-42lbs weights

  7. Top | #5

    Join Date
    Dec 2016
    Last Online
    Yesterday @ 08:44 PM
    Location
    Michigan
    Posts
    156
    Thanks
    1
    Thanked 25 Times in 19 Posts
    Fiberglass home insulation is NOT considered an acceptable fire safeing product. Its density is not high enough and its binder breaks down at less than 400 degrees F. Mineral wools are an approved fire safeing product and are used for this all the time. This void should have been sealed when the unit was installed for fire safety reasons and being a draft stop is a result. I was in the commercial and industrial insulations business for 40 years.
    Ron
    BigJim55, flyweight and tj1 like this.

  8. The Following User Says Thank You to RonPol For This Useful Post:

    96PSD (01-13-2017)

  9. Top | #6
    96PSD's Avatar
    Join Date
    Jul 2014
    Last Online
    08-07-2019 @ 09:34 PM
    Location
    East Windsor, NJ
    Posts
    444
    Thanks
    15
    Thanked 60 Times in 43 Posts
    Thanks Ron,

    I figured as much by reading a lot of information, but you know it is never spelled out exactly in black and white for the purpose you want to use it in. I wanted to check with people that are more knowledgeable in this area just in case. The great knowledge bowl of GTT.
    BigJim55 and tj1 like this.
    2014- JD 1025r
    L120 59" FEL, 260 BH, 60D MMM
    66"/54" plow with Artillian extension and rubber edge
    Artillian 36" forks
    JD 550 3PT Tiller
    54" spike aerator
    Fimco 3PT 40 gal boom sprayer
    Trac-Vac 580
    CMP 3PT 60" Dethatcher
    51" Lucknow 3PT rear snowblower
    Omni Transformer 3PT weight rack w/ 2" hitch receiver 6-42lbs weights

  10. Top | #7
    raco232's Avatar
    Join Date
    Nov 2015
    Last Online
    Yesterday @ 05:46 PM
    Location
    Memphis, Mississippi
    Posts
    562
    Thanks
    74
    Thanked 51 Times in 44 Posts
    The temp rating of Roxul is up to 2150 deg. F. I work for them in Mississippi and can tell you by their demonstrations, that temperature rating is true. There are several videos on YouTube that show the manufacturing and demonstrations. The place that I would put the insulation is at the exit (the top) of the chimney, under the rain cap. The insulation is waterproof as well as fireproof. Even though I work there, I still find it fascinating on the manufacturing process. It is very good temp, waterproof and sound deadening insulation. I even have a BBQ smoker that has Roxul insulation in every square inch of the sidewalks, even including the firebox. The smoker is painted with automotive paint, and it is not tarnished one bit.
    2012 JD2520 R4's.
    200CX Loader, 49" bucket
    Imatch quick hitch
    King Kutter 60" tiller
    Howse 60" Box blade
    Howse 16" Single bottom plow
    Dirt Dog 5 Shank Chisel Plow (60")
    Homemade 3pt suitcase weight hitch
    Homemade 3pt 1 row disc hiller
    Homemade (6) shank toothbar
    (4) 2" Motorsports Wheel Spacers
    (7) 70lb suitcase weights
    Ken's bolt on hooks
    Titan 42" pallet forks

  11. Top | #8
    tj1
    tj1 is offline
    tj1's Avatar
    Join Date
    Jan 2015
    Last Online
    Yesterday @ 04:15 PM
    Location
    ma
    Posts
    3,848
    Thanks
    264
    Thanked 301 Times in 224 Posts
    it also sounds like the damper has not been sealed. There are kits to seal the damper location when converting to a wood stove insert.. You may want to investigate that also.. As an inspector we look for the sealing of the damper as part of the approval. The damper (moving part) itself should have been removed, The other good advice you have received is to cap the top of the chimney. Watch for condensation in the chimney too, it's always a good idea to insulate the stove pipe all the way to the exit, most do not do this because of the expense but good installers do recommend this as part of their price/install.. Jeff
    Tomfive likes this.
    Jeff

    X 738 4X4/ 54" mower deck, 47" two stage snow thrower/ linear actuator spout control, Curtis hard side cab/heater, JD roof top LED work lights, Curtis fuse block, rear roof light connected to dash light switch and reverse lights, additional 20amp alternator, Curtis fast Cast 2000 sander custom fitted to tractor/ vibrator for use with dry sand, Kubota L39 TLB, JD 450 E dozer, Husky 18 horse/ 48" mower deck/Berco 42" two stage snow thrower/Berco soft side cab, Kubota RTV500-H.

  12. Top | #9
    Tomfive's Avatar
    Join Date
    Dec 2011
    Last Online
    Yesterday @ 04:17 AM
    Location
    Mid-Hudson Valley, NY
    Posts
    4,116
    Thanks
    97
    Thanked 603 Times in 469 Posts
    Just wanted to add my 2 cents. When we had out fireplace insert installed, they sealed the top of the chimney around the liner (good advice), removed the damper plate and had to cut a bit of the damper to fit the 6" liner. They put all the pieces inside/above the damper area "just in case someone decides to change back to a working fireplace", but they didn't seal the damper area with a block-off plate just stuffed some type of insulation around the liner and terracotta flue liner at the bottom. We've had no drafty issues.

    In addition, whoever built my fireplace, installed an outside air intake under the firebox with a damper flap to control the air. That was sealed shut during the installation.

    I guess it depends on where your air leak is coming from, top, leaky chimney between the firebox and top, cold air intake (if you have one)? Sealing all areas would help your problem.

    Regarding insulation on your liner, IMO, it's not necessary on the fireplace insert, I guess you'd be expected to run it long enough and hot enough that condensation shouldn't be an issue. In addition, there may not be enough room in your flue to have insulation. My fireplace flue has a 6" X 9" terracotta liner and I needed a 6" SS liner. I installed a SS liner for my oil furnace, and I did put insulation around it. 6" X 6" terracotta and 5" SS liner with 1/2" insulation. Tight fit but I got it in. My oil burner fires on and off for short periods, especially when just making hot water, and sometimes doesn't run enough to really heat up the entire chimney, so condensation would be a concern.

    So ... back to your original question, I don't know about Roxul, but I will say that I have thermocouples on my fireplace insert and the flue pipe several inches above the fire box. The hottest I've run my fireplace insert is well over 800F, never hit 900F, but I'm sure it can go that high or above. Let that be your guide for the insulation you choose.

    Again, just my 2 cents.

    BTW, don't forget to sweep your fireplace chimney at least once per year, creosote builds up and can cause chimney fires.
    Tom

    2011 1026R/R4's -- H120 FEL/49" -- 260 BH/12" -- Bro-Tek Ripper -- Artillian Forks/42" -- 244 lbs JD Rear Wheel Weights -- KBOH Hooks and Clevis' --
    Block heater -- 180* T-stat -- Evans HP Waterless Coolant

  13. Remove Advertisements
    GreenTractorTalk.com
    Advertisements
     

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •